Is there any small appliance doctors in the house?

Post by J Miller »

OT: Sorry Hobie, I just had to do that for old times sake :twisted:

As some of you know, ( and I'm sure don't care ) I've taken up a hobby fixin' and using sewing machines. Occasionally I get one that will give me a buzz when I touch it.
What I'm looking for is a place to start diagnosing it. I can check all the wiring connections (I guess that's a place to start), to make sure there's nothing wrong there, but if that don't fix it, where do I look next? I have one that will buzz me, and one that's almost a byte. :o
This happens more in the basement where there is a strange electrical thing. Lots of metal, conduits, and a bare concrete floor.

Joe
***Be sneaky, get closer, bust the cap on him when you can put the ball where it counts ;) .***
pwl44m
Advanced Levergunner
Posts: 3613
Joined: Sat Sep 04, 2010 7:48 pm
Location: East Linda Caif.

Re: OT: Is there any small appliance doctors in the house?

Post by pwl44m »

Are Your outlets Grounded ?
Perry
Perry in Bangor----++++===Calif
User avatar
J Miller
Member Emeritus
Posts: 14885
Joined: Sat Mar 31, 2007 7:46 pm
Location: Not in IL no more ... :)

Re: OT: Is there any small appliance doctors in the house?

Post by J Miller »

pwl44m wrote:Are Your outlets Grounded ?
Perry
The one the machine is plugged into is. Well the machine is plugged into an extension cord that has a built in circuit breaker. That is plugged into the grounded outlet.

Joe
***Be sneaky, get closer, bust the cap on him when you can put the ball where it counts ;) .***
pwl44m
Advanced Levergunner
Posts: 3613
Joined: Sat Sep 04, 2010 7:48 pm
Location: East Linda Caif.

Re: OT: Is there any small appliance doctors in the house?

Post by pwl44m »

Is it only the two Machines that do it ? Assuming they have original cords, check under the paper insulator to see if the wires are frayed and touching the other prong.
Perry
Perry in Bangor----++++===Calif
User avatar
pokey
Advanced Levergunner
Posts: 2704
Joined: Mon Feb 09, 2009 10:19 pm
Location: La center, wa.

Re: OT: Is there any small appliance doctors in the house?

Post by pokey »

what vintage machine?
3 wire cord [external ground]?
2 wire cord [insulated case]?

obvious stuff, you are the path to ground when you get "buzzed".
in your basement you are providing a better path, for whatever reason.
careful what you wish for, you might just get it.

"BECAUSE I CAN"
User avatar
horsesoldier03
Advanced Levergunner
Posts: 2072
Joined: Sat Sep 08, 2007 7:32 pm
Location: Kansas

Re: OT: Is there any small appliance doctors in the house?

Post by horsesoldier03 »

If your getting buzzed it aint grounded properly. The question is "WHERE IS IT NOT GROUNDED PROPERLY"? I would go to True Value or other place with electrical stuff and get a Receptical Test Plug that you plug into the outlet.
http://en.wikipedia.org/wiki/Receptacle_tester
http://www.amazon.com/Electrical-Recept ... B0012DHVQ0

If it aint the wall socket, it is probably a spliced wire on that old sewing machine.
“Gun control is like trying to reduce drunk driving by making it tougher for sober people to own cars.”
pwl44m
Advanced Levergunner
Posts: 3613
Joined: Sat Sep 04, 2010 7:48 pm
Location: East Linda Caif.

Re: OT: Is there any small appliance doctors in the house?

Post by pwl44m »

Joe, I remember Our first encounter - No I don't think U R a blithering Idiot. But Are You sure Your outlets are grounded or are You assuming because they have 3 prongs ? One of those outlet testers like horsesoldier mentioned would tell U for sure.
Perry
Perry in Bangor----++++===Calif
williamranks
Levergunner 3.0
Posts: 596
Joined: Sun Sep 16, 2007 9:09 am
Location: Camp Verde, AZ

Re: OT: Is there any small appliance doctors in the house?

Post by williamranks »

How many prongs on the sewing machine cord?
Bill Ranks
I never learned from a man who agreed with me.
Robert A. Heinlein
User avatar
J Miller
Member Emeritus
Posts: 14885
Joined: Sat Mar 31, 2007 7:46 pm
Location: Not in IL no more ... :)

Re: OT: Is there any small appliance doctors in the house?

Post by J Miller »

pwl44m wrote:Is it only the two Machines that do it ? Assuming they have original cords, check under the paper insulator to see if the wires are frayed and touching the other prong.
Perry
Perry,
Only two that I can say for sure. Maybe three. But since we have over 30 and most don't do it, it's kind of a icky feeling when it happens.
I should say that those machines that are doing this are very old.
Two are pre WWII, one is maybe 100 years old.
>One of the machines has been completely rewired from the inside of the motor out.
>One has a new cord set from the motor block to the wall and a new foot controller as well. The light has been rewired too, but the motor is original. This is the one that started this thread.
>The last one has been completely rewired from the block out to the wall and foot controller.
pokey wrote:what vintage machine?
3 wire cord [external ground]?
2 wire cord [insulated case]?

obvious stuff, you are the path to ground when you get "buzzed".
in your basement you are providing a better path, for whatever reason.
Pokey,
Very old, I covered that above.
All have two wire cords. None of our machines up to the newest one made in the mid 80s have three wire cords.

I think, I did a thread some time back about the first machine wiring. But it's been a very long time. This basement has a lot of metal AC ducting in the end my work area is in. I can touch a volt meter to the ducting and to a metal object plugged in, running or not and get nearly a full voltage reading.
The link to it was on our dead hard drive.

It's like the air in the basement is the conduit as much as anything else.

I can take the machines upstairs and get little or no buzz off the same machines.
horsesoldier03 wrote:If your getting buzzed it aint grounded properly. The question is "WHERE IS IT NOT GROUNDED PROPERLY"? I would go to True Value or other place with electrical stuff and get a Receptical Test Plug that you plug into the outlet.
http://en.wikipedia.org/wiki/Receptacle_tester
http://www.amazon.com/Electrical-Recept ... B0012DHVQ0

If it aint the wall socket, it is probably a spliced wire on that old sewing machine.
horsesoldier03,
That sounds like a good idea. I'll pick up one of those testers next trip to the hardware store.

I'm pretty careful with my wiring, but I suppose a stray wire could exist. Another thing to check.
pwl44m wrote:Joe, I remember Our first encounter - No I don't think U R a blithering Idiot. But Are You sure Your outlets are grounded or are You assuming because they have 3 prongs ? One of those outlet testers like horsesoldier mentioned would tell U for sure.
Perry
Perry,

Your memory is better than mine ~or~ do I really want to remember?
And sometimes even I think I'm a blithering idiot. I just try to not to do it too often.
The one the extension cord is plugged into is a three wire system ... I'm semi sure. I haven't taken the plate off the box to look, but it's a 2 wire with ground cable going from the breaker box to the outlet. No guarantee the ground wire is hooked up though.
Something else to check.
williamranks wrote:How many prongs on the sewing machine cord?
All are two wire systems.

Joe
***Be sneaky, get closer, bust the cap on him when you can put the ball where it counts ;) .***
User avatar
olyinaz
Advanced Levergunner
Posts: 3978
Joined: Sat Nov 28, 2009 2:19 pm
Location: Tucson, AZ

Re: OT: Is there any small appliance doctors in the house?

Post by olyinaz »

The problem could be inside motor no? Something grounding to the housing and then through the mounting points to the sewing machine frame?

Oly
Cheers,
Oly

I hope and pray someday the world will learn
That fires we don't put out will bigger burn

Johnny Wright
User avatar
J Miller
Member Emeritus
Posts: 14885
Joined: Sat Mar 31, 2007 7:46 pm
Location: Not in IL no more ... :)

Re: Is there any small appliance doctors in the house?

Post by J Miller »

Could be.

That I can check with a meter.

Joe
***Be sneaky, get closer, bust the cap on him when you can put the ball where it counts ;) .***
User avatar
J Miller
Member Emeritus
Posts: 14885
Joined: Sat Mar 31, 2007 7:46 pm
Location: Not in IL no more ... :)

Re: Is there any small appliance doctors in the house?

Post by J Miller »

Well this is interesting, but not unexpected.

I brought the machine in question up stairs.
Image
She's a White Dressmaster made in the 30s as far as I can find out, and yes she's OD green :mrgreen:

The using my continuity meter I checked for any form of continuity between the cord block and the rest of the machine. Since the contacts in the cord block are directly connected to the motor wires if there is bad insulation inside the motor and it's making contact the meter would show it.
Nothing. OL all the way across.

So then I plugged it in to a non grounded extension cord which was plugged into a non grounded outlet and there was no buzz.

What ever the problem is, it is in the basement.

Joe
***Be sneaky, get closer, bust the cap on him when you can put the ball where it counts ;) .***
Retro
Levergunner 2.0
Posts: 146
Joined: Tue Dec 18, 2007 11:42 am
Location: Cape Town, South Africa

Re: Is there any small appliance doctors in the house?

Post by Retro »

Build yourself an outlet with a ground circuit interrupter (we call 'em earth leaks, I think you call 'em GFCIs or some such). That'll spare you the buzz and mebbe a trip in a white van with a cross on the side.
User avatar
Griff
Posting leader...
Posts: 20864
Joined: Sat Mar 31, 2007 4:56 pm
Location: OH MY GAWD they installed a STOP light!!!

Re: Is there any small appliance doctors in the house?

Post by Griff »

Aye, Joe, it sounds like the wiring into the basement is butt backwards... or simply isn't going to ground as it should. Or in one socket or another the hot side is touching the case. You have metal boxes, or plastic ones?

My F-I-L and B-I-L were excellent electricians... wished I learned more from them when I worked for them in college... but hating that "buzz" I never trusted them too much. They LIKED working on hot circuits... they always said they could tell when stuff was right that way! Not me. Getting knocked on my kiester once was enough to learn me!
Griff,
SASS/CMSA #93
NRA Patron
GUSA #93

There is a fine line between hobby & obsession!
AND... I'm over it!!
No I ain't ready, but let's do it anyway!
User avatar
J Miller
Member Emeritus
Posts: 14885
Joined: Sat Mar 31, 2007 7:46 pm
Location: Not in IL no more ... :)

Re: Is there any small appliance doctors in the house?

Post by J Miller »

This house was built in the 50s. By the looks of the materials and construction we're pretty sure it was not built by a construction company. The wiring is at least three generations. The newest appears to be the circuits we are using for the machines. This is the circuit the wash machine is on as well.

If the wires are backwards or not properly grounded it is the landlords responsibility to fix them. And unless one of us is killed he couldn't care less. Typical landlord.
We are planning to buy one of the little testers mentioned above, and then we should know.
Until then I figure we'll have to move the machines away from those circuits.

Joe
***Be sneaky, get closer, bust the cap on him when you can put the ball where it counts ;) .***
User avatar
pokey
Advanced Levergunner
Posts: 2704
Joined: Mon Feb 09, 2009 10:19 pm
Location: La center, wa.

Re: OT: Is there any small appliance doctors in the house?

Post by pokey »

J Miller wrote:
This basement has a lot of metal AC ducting in the end my work area is in. I can touch a volt meter to the ducting and to a metal object plugged in, running or not and get nearly a full voltage reading.


Joe
revisit this.
could be it's not the machines.
sounds like your ductwork may be hot.
careful what you wish for, you might just get it.

"BECAUSE I CAN"